Block of flats (PB) in 1990. 3 floors with one staircase and front and rear exits to ether car park or street. (1 mtr from bottom of stairs) 

On ground and first floor only there are corridors no more than 8 mtrs long containing 4 flats.

Each corridor has a set of double doors from new. These doors are solid 44mm Windsor style doors with Georgian wired glass as from new.

All frames have intumescent seals and one door has the same along one edge. All in good condition. Hinges were changed to G13 Fire Rated hinges 2 years ago , after a FRA.

All flat doors have certified FD30 doors with overhead closers, G13 Fire rated hinges, and seals and conform to all latest specs (after Door assessment)

We are now being told that the` Windsor style` cross corridor doors MUST be replaced with new doors.

No reason is being given other than ` old ones do not comply`

The doors have stickers (albeit 2017) from a fire door company saying that they were approved Fire Doors, in addition to having passed all previous FRAs. with the upgrade of the new hinges.

Is there or has there been any change in policy and Law for the Managing agent to now enforce this??

Posted
4 hours ago, delboy said:

We are now being told that the Windsor style cross corridor doors MUST be replaced with new doors.

No reason is being given other than ` old ones do not comply`

There has been no such change.  I would push them about exactly why these doors do not 'comply' and what it is they do not 'comply' with.

Posted

Here is an image of the doors as they are today.

I heard that the company quoting for the job has spoken with a local Safety Officer (no idea who they are talking about) presumably from the council, but these flats are ALL private and nothing to do with the council.

Doors are all sound but at 30 years old do have the odd nick on them, but thats about it as far as I can see.

IMG_20211021_153616.jpg

Posted

They do look like the original fire doors that are to the standard of the time with the upgrades as already mentioned.

They would be acceptable under both the existing flats guidance and based on the draft for consultation would still be acceptable under the new small blocks of flats guidance produced to account for the Fire Safety Act's amendment of the fire safety order.

Unless you see something in writing from the Council that you have verified is really from them I'd do nothing and even if something does then I'd ask a competent person to look at their rationale & put forward a  rebuttal if needed.

Could be a confidence trick, wouldn't be the first fire safety related one I've heard of. 

Posted

Thank you so much for your replies.

Further I have found the detailed wordings from the Door assessments.

I cannot look at all cross doors in all flats but I can look at the double doors shown on my image.

So referring to their observations regarding these particular doors they comment as follows:

 Has the door got a Fire Door label?................................................................Answer....,solid construction..........No Fire label.................NEW DOORS REQUIRED

If not, can you confirm it is a nominal Fire Door.............................................Answer...Yes.

Is the Frame firmly attached to the wall?........................................................Answer....No...gaps between wall and frame..........Install Fire stopping

Is the frame/door leaf consistent 3mm.?........................................................Answer....NO.......Result....Will be resolved when fitting new doors.

Are the intumesent/cold smoke seals in place?............................................Answer.YES...........result....supply and install new smoke seals !!!!

No intumesecent seals continues to the glass..............................................Answer......Not required as new doors will be fitted

That is a summary of any negative results to their questions.

I would admit that in my own opinion there is minor works to satisfy some of issues raised.

The only one I am unsure about is the Intumescent seals to the glazing.

I guess that If that in itself is not up to standard then any other problem is irrelevant??

Posted

It's still not a requirement for the door to have a certification mark, it makes identifying the door more difficult but isn't the end of the world.

It's far easier to rebead the glazing with the correct intumescent than replace the door and frame (if they don't replace the frame then any new door certificate would be invalid as certification is for door sets (frame, ironmongery, etc) not just the door.

Posted
16 minutes ago, AnthonyB said:

It's still not a requirement for the door to have a certification mark, it makes identifying the door more difficult but isn't the end of the world.

It's far easier to rebead the glazing with the correct intumescent than replace the door and frame (if they don't replace the frame then any new door certificate would be invalid as certification is for door sets (frame, ironmongery, etc) not just the door.

Thanks, really interesting...they are actually quoting for the doors like this (image attached from your site), and are saying that they can no longer use doors like the existing ones? ...........Not allowed. (local safety officer, still unknown)

As you can appreciate they will just not match up in any way and look hideous, without matching frames, and then the cost will more than double

But if they are NOT allowed, how can they leave the side glazed frames in place? Which part is not liked....a 44mm solid hardwood door or the glazing.

And you can see that the frame also has a side glazed attached to the wall. No mention of new frames is mentioned at all, despite being space to say that (well not until they start I wouldn`t be surprised). In fact they do mention that sealant is needed between frame and wall, for which they have included a cost £130 per door frame

This is fast becoming an issue. Section 20 has been issued and looks like they will railroad this through.

 

 

 

door.jpg

Posted

From what you say, Delboy, I am struggling to see how the fire door assessor has reached the conclusion that new doors are required. That's not to say that some upgrading wouldn't be recommended.

Posted
On 28/10/2021 at 06:10, Neil ashdown said:

From what you say, Delboy, I am struggling to see how the fire door assessor has reached the conclusion that new doors are required. That's not to say that some upgrading wouldn't be recommended.

Hi

     Yes, me too, and other leaseholders.

I have no problem is some extra work being. The really annoying thing is that on the last FRA in 2018, things like the hinges were reported, and all the work was done, at some considerable cost.

New managing agents since then, of course they use their own tame Fire Risk assessors, different assessor, different result !!! 

I can see this palava going on at each FRA in future, always finding something to spend our money on.

Fair enough if its really needed, but........................

 

  • 1 year later...
Posted

Here is an update to this now old post.

After many attempts to get the MA to see sense, they finally agreed to meet another Fire company to look at the cross lobby doors...............upshot of that is that they were told that new doors are not needed, due to the distance of flat doors from stairways ...so a huge saving to leaseholders in unnecessary expense, due to dogmatic approach bt MA.

However despite that, no works have, as yet, been carried out from the FRA recommendations  done in June 2020 !!!!!

Now they are telling us that we must have annual checks, both internal and external. to all flat doors

So now another discussion ensues........The blocks of PB flats are less than 11mtrs tall, at the height of the top floor floor (In fact its only a 3 storey property, GF/FF/SF).

As I read the Regulation 10 of the updated Fire Safety report (Feb 2023) only if a building is more than 11mtrs tall (at level of top floor floor) is an annual check required.

Am I reading this all wrong? 

Of course from my viewpoint I would say that any/all occupiers, whether owner  occupiers or tenants should do this every day, let alone every year. As far as I see it it is just another tick box exercise, to cover the Freeholder, because like an MOT on a car, its only good on the day its done, and therefore, only suggests safety on 1 day out of 365.t day

Posted

The Government guidance clearly states that buildings with the floor of the top storey under 11m are not exempt from the need for fire door checks under Article 17 of the Fire Safety Order, only that the frequency of those checks is not prescriptive as per the Fire Safety (England) Regulations, for example a smaller block may decide through their risk assessment to only check communal doors 6 monthly and only check a percentage of flat doors annually rather than trying to check all of them.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...