AlwaysLearning Posted September 17, 2021 Report Posted September 17, 2021 Help as for the love of looking i cant find and answer to this?! A pub has a LG bar area with 5 exits, three are close to one another and have to be discounted, the remaining two lead to a single protected stairwell, each door has the capacity for 100 as opens outwards and are 800mm each. The shared escape stairwell is 830mm and am concious of bottlenecking as in theory the doors combined allow a total of 200 people, do i use the calculation of just 100 people on the same grounds as a door width capacity or is there an alternative calculation? Any help greatly appreciated. Quote
Tom Sutton Posted September 21, 2021 Report Posted September 21, 2021 I am not aware of any alternative calculations and your calculations appear to be correct but trying to imagine the layout is difficult and without a full survey or detailed plans it is impossible to give you a definitive answer. Quote
Mike North Posted September 21, 2021 Report Posted September 21, 2021 I think you will find your limiting factor will be the the capacity of the stairwell. Quote
AlwaysLearning Posted October 5, 2021 Author Report Posted October 5, 2021 Thanks Mike / Tom, much appreciated......sometimes you do question yourself! Quote