Jump to content

Recommended Posts

Posted

We are currently refurbing a single story building which has 3 corridors approximately 35m in length running in parallel between the final exits.  We are installing FD30S doors as approximately the midpoint of each corridor.  The issue is that at the midpoint is another corridor that connects the three corridors but is not connected to a final exit (basically |-|-|) we can either put a door at the midpoint of each (2 doors) or at the end (3 doors).  Does anyone have any suggestions or an alternative, currently the walls are not full height and so require fire stopping.

  • 2 weeks later...
Posted

What is the fire doors being install for, and a sketch would easier to understand than your description also what guidance is the premises subject to.

  • 2 weeks later...
Posted

In my opinion two FD30s doors at the intersection of the west and cross corridor also similar arrangement for the east corridor. Also three FD30s doors at the intersection of the central and cross corridor, would achieve acceptable travel distances to places of relative safety/ultimate safety. What I am unable to establish if it is possible for a fire to pass from any  section of corridor to another via the office space/sales area.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...