In a circa 1987 five story block of older persons sheltered flats there are AOVs at the end of the corridors with OVs directly below them. As I understand it, current principle is the AOVs should only open on a fire floor to prevent ingress of smoke ventilated from a lower floor into a higher floor. Where there are OVs directly below the AOVs that are used for day-to-day ventilation and generally left open, this seems somewhat pointless. In these circumstances should the aspiration be for the OVs to be sealed / replaced by AOVs or is it the case that as the building was approved at the time of its construction it remains acceptable? 

Posted

Are these in windows on an external wall? It's more of an issue with internal smoke shafts, where incorrect C&E on the system has led to rapid spread of smoke through all floors.