I have 6 Identical large dinners; the latest building has FD30S double swing doors between the diner and kitchen the rest have FD60S.  All were built to 2007 regs. The doors are now at the end of life, can I replace them with

·         The regulatory requirement is for a FD30 door to be installed.

·         An FD60 rated door (as installed in 5 of the diners) configure as an FD30 to provide a more robust solution.

·         All double doors are to installed with

  • A back-check mechanism to stop the over extension of the hinge on opening.
  • Automatic hold-open connected to the fire alarm system with a timed release so that the doors return to the closed position when the diner is unoccupied.  

·         Door protection on both faces of the door to a height of 25mm above the height of the kitchen trollies.

·         The glazing with any associated beading shall not be installed within 25mm of the door protection.  

·         Leading edge protection shall be installed.

 

Posted

I think what you are proposing sounds reasonable but reducing 60 minute protection to 30 minute protection may need building regs approval you should consult with building control.

Posted

And you should have a Fire Risk Assessment in any case and a significant change, such as altering the standard of fire protection, requires a review. Building Regulations and Fire Regulations are totally separate entities. 

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...