Rob64 Posted December 2, 2020 Report Posted December 2, 2020 Can anyone signpost me to the relevant guidance / regulations on inspection and / or drop testing of fusible fire dampers on bin chutes. I understand it is somewhere within BS:9999 (2017) but I’ve trawled through it without success. Thanks Quote
AnthonyB Posted December 3, 2020 Report Posted December 3, 2020 Annex I I.7 (e) would seem appropriate (annual) - they operate similarly to mid duct shutters Quote
Rob64 Posted December 11, 2020 Author Report Posted December 11, 2020 Many thanks Anthony. I’ll check it out. Quote