Meady Posted October 11, 2020 Report Posted October 11, 2020 Does anyone know if self-testing emergency escape lighting still needs a 3-hour discharge test each year?? We're looking at BS5266-1 and BS EN 50172 and we cant see where it mentions self-testing systems? Any help / guidance much appreciated. Quote
AnthonyB Posted October 12, 2020 Report Posted October 12, 2020 Yes, but they do that automatically and report if they fail (either to the control panel if an integrated network or via the coded LEDs on the fitting if self contained). Just inspect them visually (& the control panel where fitted) monthly and act on the faults indicated (if any) Quote
Meady Posted October 19, 2020 Author Report Posted October 19, 2020 On 12/10/2020 at 20:30, AnthonyB said: Yes, but they do that automatically and report if they fail (either to the control panel if an integrated network or via the coded LEDs on the fitting if self contained). Just inspect them visually (& the control panel where fitted) monthly and act on the faults indicated (if any) Thank you as always AnthonyB - much appreciated. Quote