Jump to content

Recommended Posts

Posted

Does anyone know if self-testing emergency escape lighting still needs a 3-hour discharge test each year??

We're looking at BS5266-1 and BS EN 50172 and we cant see where it mentions self-testing systems?

Any help / guidance much appreciated.

Posted

Yes, but they do that automatically and report if they fail (either to the control panel if an integrated network or via the coded LEDs on the fitting if self contained).

Just inspect them visually (& the control panel where fitted) monthly and act on the faults indicated (if any)

Posted
On 12/10/2020 at 20:30, AnthonyB said:

Yes, but they do that automatically and report if they fail (either to the control panel if an integrated network or via the coded LEDs on the fitting if self contained).

Just inspect them visually (& the control panel where fitted) monthly and act on the faults indicated (if any)

Thank you as always AnthonyB - much appreciated.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...