T.Pedersen Posted September 21, 2020 Report Posted September 21, 2020 Hi, I vaguely remember seeing a recommendation that the 5kg variant instead of the 2kg C02 should be installed where there is 400V+ present; is this correct as I can not find reference to this now? Thanks Quote
AnthonyB Posted September 22, 2020 Report Posted September 22, 2020 No, it's an urban myth. The only reason why you might go for a 5kg for an electrical risk is if the size of the enclosure is such you need the larger volume of gas to flood it adequately. Quote
T.Pedersen Posted September 22, 2020 Author Report Posted September 22, 2020 many thanks for clarifying Quote