bob2813 Posted April 14, 2020 Report Posted April 14, 2020 Hi, I am looking for guidance on the type of packer that can be used behind frame fixings for FD30 doors. I read that plastic packers can be used on FD30's. just not FD60's - is that correct ? Can plastic packers be used ?, if an appropriate 10mm intumiscent mastic bead is run round the gap between frame and supporting construction, assuming gaps on average between are 5-10mm, packers chiselled back where necessary to allow the depth of a 10mm mastic bead, an architrave placed on top. I do not yet own a copy of "BS 8214:2016 Timber based fire door assemblies Code of practice", but will place an order shortly (seems curious a hard copy version is no more cost than a PDF). Will this document contain the information I require regarding packers /. I have read several other documents, ie: ASDMA 'Best Practice Guide' and 'Guidance on Fire Door Installation', BWF 'Fire Door and door sets, Best Practice Installation', and the relevant Certifire certificate documents for the doors. The only reference I can find in any of these documents for packers is 'Proprietory trouser leg packers are best', and 'Timber Packers should be applied behind fixings' (Do not use plastic packers.)' - from a practicle point of view you are not going to find a 1mm timber packer. I have spoken to the manufacturer of the Fire Door lining (Arbor Forest Products Limited) we are to use, but they report the Linings are not tested with any gaps in the surrounding construction. I understand a product called Blue 60 is for 60 minute FD's but it is not Certifire Certificated, which I understand it needs to be for the mix and match specification of FD components under the Certifire certification process. Thanks Quote
Safelincs Posted April 15, 2020 Report Posted April 15, 2020 Hi Bob There are specific 60 minute intumescent plastic packers for fire door gaps available. Harry Quote
Neil ashdown Posted April 16, 2020 Report Posted April 16, 2020 Hi Bob, The gap between the door frame and surrounding wall construction would typically be between 5mm and 20mm. BS 8214 is a very useful document in ensuring compliance of this work. Timber packers / folding wedges are preferable to plastic packers but plastic may be used so long as they are cut back by at least 10mm on both sides of the frame and covered over with a bead of intumescent mastic at least 10mm thick. Fire foams tested to BS 476 part 22 or EN1634-1 may be used but only within the scope of the fire test evidence, this may mean using dedicated packers as part of the tested fire sealing system. The image below illustrates the door frame to wall gap tightly packed with mineral wool but note that a 10mm bead of intumescent mastic is required to BOTH SIDES! Hope this helps, Neil. Quote
bob2813 Posted May 10, 2020 Author Report Posted May 10, 2020 Thank you both for your replies. Out of interest I have done my own tests on Fire Foam and plastic packers, its an unscientfic work, but I will post up images of the results shortly for what its worth. For now I will stop using B2 Fire Foam for use in linear gaps, and use mineral wool instead. Architrave Architrave is fitted to the door frame surround, but my reading of the door certificate and test report, and other documentation seems not to give definitive credance to the protection provided by the architrave, almost suggesting that the test results should be viewed as if Architrave is not fitted, yet other writings suggest a 19mm thick architrave does provide some protection. Could I draw from this that, as archtrave comes in many differing styles (Ovolo, ogee, Torus etc etc) the thickness of these at the point of nailing (and gap covering) is often less than 19mm, usually nailed with thin panel pins, and a softwood, so its not always viewed as offering reliable protection ... and hence the need for mastic in any gaps behind. Building Control How much should you rely on Building Control to advise on fire protection in a buildings fabric, if you seek approval from them for a specific solution to a problem (ie pentrations through a 60 minuite ceiling, and glass in a 60 minute wall), and they approve your proposal, and it is installed correctly, can you be confident they will advise correctly, or should you seek more specialised advice. I am using a large national private Building Control company. Fire Protection Details. Is it normal for an architect to advise on Fire matters with Fire Protection Details on BC plans, or should one look to Building Control to advise, do Building Control look over plans prior to works and over rule/make additional direction on Fire matters to that of the architect. Quote
Neil ashdown Posted May 11, 2020 Report Posted May 11, 2020 Thank you Bob, glad to be of use. I will do my best to take your questions one by one.............. ArchitraveArchitrave is fitted to the door frame surround, but my reading of the door certificate and test report, and other documentation seems not to give definitive credance to the protection provided by the architrave, almost suggesting that the test results should be viewed as if Architrave is not fitted, yet other writings suggest a 19mm thick architrave does provide some protection.Could I draw from this that, as archtrave comes in many differing styles (Ovolo, ogee, Torus etc etc) the thickness of these at the point of nailing (and gap covering) is often less than 19mm, usually nailed with thin panel pins, and a softwood, so its not always viewed as offering reliable protection ... and hence the need for mastic in any gaps behind.A: Fire doors are fire resistance tested without architraves fitted. Generally, for the reasons you state, the architrave should not be relied upon as a contributor to fire performance. Clearly, though, where architraves are securely fitted as described in BS 8214 they would likely enhance the fire resistance performance of the door. Building ControlHow much should you rely on Building Control to advise on fire protection in a buildings fabric, if you seek approval from them for a specific solution to a problem (ie pentrations through a 60 minuite ceiling, and glass in a 60 minute wall), and they approve your proposal, and it is installed correctly, can you be confident they will advise correctly, or should you seek more specialised advice. I am using a large national private Building Control company. A: The Building Control officer may not be a specialist in passive fire safety, their job is to see that the works meet the requirements of the Building Regulations. With that in mind, I am of the opinion that it is better and safer to consult a specialist to advise on a particular fire resistance issue. Fire Protection Details.Is it normal for an architect to advise on Fire matters with Fire Protection Details on BC plans, or should one look to Building Control to advise, do Building Control look over plans prior to works and over rule/make additional direction on Fire matters to that of the architect. A: Sorry, I can't answer that one as it's beyond the level of my experience in Building Control matters. Quote
AnthonyB Posted May 11, 2020 Report Posted May 11, 2020 Considering how many newsworthy fires in defective buildings, newsworthy critical defects uncovered and the general experience of the fire safety sector I wouldn't rely on an AI or BCO for fire safety advice - too much stuff gets signed off only later to be revealed to be substandard and need reworking at great expense. Quote
Guest Paul Church Posted October 19, 2020 Report Posted October 19, 2020 On 16/04/2020 at 07:33, Neil ashdown said: Hi Bob, The gap between the door frame and surrounding wall construction would typically be between 5mm and 20mm. BS 8214 is a very useful document in ensuring compliance of this work. Timber packers / folding wedges are preferable to plastic packers but plastic may be used so long as they are cut back by at least 10mm on both sides of the frame and covered over with a bead of intumescent mastic at least 10mm thick. Fire foams tested to BS 476 part 22 or EN1634-1 may be used but only within the scope of the fire test evidence, this may mean using dedicated packers as part of the tested fire sealing system. The image below illustrates the door frame to wall gap tightly packed with mineral wool but note that a 10mm bead of intumescent mastic is required to BOTH SIDES! Hope this helps, Neil. Very interesting comment Neil regarding cutting back packers 10mm. Is there anywhere I could find literature to support this? Regards & thanks in advance. Quote
Neil ashdown Posted October 21, 2020 Report Posted October 21, 2020 Hi Paul, Fire Door Inspection Scheme Transition Module. Should I come across this elsewhere, I will post here. Quote
Guest Harry roberts Posted July 6, 2021 Report Posted July 6, 2021 Hi it’s different question to what has been asked but fitting of fed or communal fd60/30 can pvc architraves be fitted. Obviously Olof sufficient packers and fire mastic have been used. It would be very helpful to know. Thanks in advance Quote
Neil ashdown Posted July 30, 2021 Report Posted July 30, 2021 There is no reference to the use of PVC architraves in the BS 8214: 2016 Timber-based fire door assemblies - code of practice. So with reference to Flat Entrance Doors (often composite construction) I would consult the door manufacturer. Doors in communal areas are likely to be timber-based doors, therefore I would use timber-based architraves. Quote