Guest Kate Posted February 25, 2020 Report Posted February 25, 2020 Hello, we have a cabin inside a warehouse near a fire door. we are planning to put a wall up and an extra door in the cabin, so customers can walk straight in through the fire door into the cabin without being able to go in the warehouse. there are 2 other fire exits in teh warehouse and a roller shutter door at the front. Attached are some before & after plans... We would basically be diverting the fire escape route for the warehouse through the cabin. But not sure if this is legal? Be glad of any advice. thanks Quote
Tom Sutton Posted February 26, 2020 Report Posted February 26, 2020 Some fire risk assessors would be a little concerned but providing you maintain an escape route of 1050 mm and level going, you appear to conform to article 14 of The Regulatory Reform (Fire Safety) Order 2005. Check this out with your FR assessor. Quote
Lyledunn Posted March 14, 2020 Report Posted March 14, 2020 Given the availability of two other exits, I would agree with Tom. However, I would formally risk-assess the situation and record as an addendum to the FRA. Further, it could be construed as a matter that would require LABC approval through Building Control. An application in that direction, even if it is a regularisation, may be prudent. Quote