If the door leaf can be identified to the manufacturer or it's fire resistance performance certification it should be possible to check the lock requirements.  Maybe the door leaf has been over-morticed at the keyhole and lock-case?

Surprised at the use of spring hinges on such a critical fire door, usually a controlled self-closer would be used meeting the requirements of EN1154 minimum power size 3 .  At the very least, I would check that the door self-closes reliably to the door frame rebate stop completely from any opening position in a safe and controlled closing action. 

  • 2 weeks later...
  • Replies 106
  • Created
  • Last Reply

Top Posters In This Topic

Posted

The Door & Hardware Federation Code of Practice: Hardware for fire and escape doors. Says that spring hinges that are purely spring urged are unable to comply with BS EN1154 and therefore should not be used for fire doors.

A suitable closer that complies with BS EN 1154 should be fitted.

The lock should be CE marked and suitable for use with a fire door, there are a number of fire rated locks on the market with the older style 3 lever 5 lever key available so it possible the one you have is suitable as long as it is correctly fitted and CE marked.

 

 

  • 10 months later...
Guest Dan1234
Posted

Hi, I have a quick question if anybody can help. I know you need a 30 minute fire door from garage to house, but would this also be the case if the garage door opens into a conservatory? The conservatory is still closed off from the main house with a double glazed aluminium patio door. thank you in advance

  • 1 month later...
Posted

Hi. I have converted part of our integral garage into a utility room. I have built a stud wall to separate from the garage. I have also raised the level of the floor in the new utility room to the same level as the Kitchen. I am now in the process of replacing all of the internal dooors. Do I need to keep the fire door that did go in to the garage or can I now fit a standard internal door. 
 

many Thanks

Posted

On the basis that there is still part of the integral garage present (but smaller than it used to be), then the separating wall needs to be suitably fire rated and if there's a door in that wall it should be minimum FD30(s) self-closing. Refer to Approved Document B of the Building Regulations in England. https://www.gov.uk/government/publications/fire-safety-approved-document-b 

  • 10 months later...
Guest Seamonkey22
Posted

Hi, I would like to put a door between my porch into the garage. The porch was added recently, so there is still the original front door into the house as well as a new front door on the porch. Do I need a fire door seeing as the original front door is still in place?

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...

×
×
  • Create New...