Guest Gary Madgwick Posted November 6, 2019 Report Posted November 6, 2019 We are designing a three storey, timber frame house that needs FD30(s) fire doors but we are also fitting an MVHR system which needs a 10mm ventilation gap under the doors which conflict with Building Regulations. We have looked around for doors and spoken to many companies and all have not come across this before. MVHR in 3 storey cannot be new? One company suggested we use a sprinkler system. Any ideas would be welcome! Quote
Neil ashdown Posted November 7, 2019 Report Posted November 7, 2019 For FD30s doors, Building Regulations ADB require compliance with BS 8214:2016 in terms of the threshold gap. Quote
Tom Sutton Posted November 7, 2019 Report Posted November 7, 2019 Where did you get, you require FD30s in a dwelling house my reading of Approved Document B (Fire Safety) Vol 1 Appendix C, table C 1, only the door between a dwelling house and an integral garage requires a FD30s fire door with self closer. As FD 20 are not readily available so you could use FD 30 fire doors and this could allow you some options regarding the ventilation. 11. In a dwelling house: Euro BS 476 p 22 a. between a dwelling house and a garage. FD 30 S a(2) FD 30 S(2) b. forming part of the enclosures to a protected stairway in a single family dwelling house E 20 FD 20 c. within any fire resisting construction in a dwelling house not described elsewhere in this table. E 20 FD 20 Quote
Neil ashdown Posted November 8, 2019 Report Posted November 8, 2019 So if restricted cold smoke spread is not a requirement for your design, FD30 doors may be used instead of FD30s doors. Many FD30 doors permit a 10mm gap at the threshold, check with the particular fire door manufacturer. Quote
Recommended Posts
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.