Guest Sarah Posted July 23, 2019 Report Posted July 23, 2019 We have just had the emergency lighting at our premises tested in house (small system). Most of the lights were fine, but a couple were not at full brightness at the end of 3 hours. So the lights were functioning, but only at say 25% capacity after the full 3 hours. Is this acceptable, as they were still lit, do they all need to still be at full brightness? Quote
AnthonyB Posted July 23, 2019 Report Posted July 23, 2019 They need to meet the minimum lighting level for the area - e.g. 1 lux on escape routes, 0.5 lux for open areas, etc. Quote
Recommended Posts
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.