Modular Interiors Posted June 13, 2019 Report Posted June 13, 2019 Good Afternoon all, Please see below my query, any advice or guidance you can give will be helpful. With regards to commercial office buildings, are there an BS standards or regulations that permit installing a 1hr fire rated door into a 2hr fire rated wall? I understand as a industry rule of thumb this is the case but cannot find any documentation to back it up? Hope you can help. Jordan Quote
Tom Sutton Posted June 13, 2019 Report Posted June 13, 2019 Check out Approved Document B (fire Safety) volume 2: Premises other than Dwelling Houses page 134 Compartment walls this maybe what you are looking for. Quote