Jump to content

Mr


Recommended Posts

Guest Isafety conscious
Posted

Can anyone please help.  I have been advised that my fire alarm does not comply. It only has one sounder circuit. Is this correct or is there any regulations etc to say I have to have two

Posted

For a very long time BS5839-1, the standard for fire alarm systems, has required 2 sounder circuits on fire alarm systems.

Whilst a BS is not law, it is generally used as a benchmark for legal compliance and if you wish to vary from it (which you can legitimately do in some circumstances) you have to justify why the departure still provides an adequate level of safety.

With one circuit there is a risk that if something goes wrong with it then you will have no warning at all of a fire - with a second circuit at least you will get partial warning.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...