Guest steve
Posted

Hola, I have an office that is approximately 220m2, there are enough fire exits (4), using the occupancy factor from ADB of 6.0 this gives a figure of 37.(rounded up).

This does not seem a lot considering the size. Am I missing something? Is there any movement on occupancy ratio that I can use.

Many thanks Steve

Posted

Occupancy factors are required, when you have an empty space and need to calculate the number of persons you have to provide an MoE for, so you need the MoE for 40 persons. If you can provide MoE for more, then you could have more depending on health and safety, so you need to check out the Workplace (Health, Safety, and Welfare) Regulations 1992 10. Room dimensions and space, to check out how many you can have, its a combination of the two.