Guest nick morrell Posted April 24, 2019 Report Share Posted April 24, 2019 hi all, im after some advice on access for fire dampers. we recently had a company in to carry out fire damper maintenance and a lot failed because of not having access panels either side of the damper. they did all have at least one and you could drop test it and reset it, but they mark it down as a fail. is it change in legislation or have they always needed 2 points of access? the building was built and signed off in 2009. thanks in advance Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted April 25, 2019 Report Share Posted April 25, 2019 The guidance used will Building Regulations which is likely to be Approved Document B (fire Safety) volume 2: Premises other than Dwelling Houses so check out page 86 which should indicate what was require during construction. All the guidance used for fire dampers is indicated in that section. Check out http://www.asfp.org.uk/slides/The risk assessment of fire damper installations.pdf and http://asfp.associationhouse.org.uk/default.php?cmd=210&doc_category=123. Quote Link to comment Share on other sites More sharing options...