We have converted two 40 foot shipping containers (joined together along the long side, creating one area approx 40' x 20') in to an Engineering workshop. There is one main point of entry/exit, through a normal style door with a door handle at one end. 

Do we need a 2nd exit door available for fire regs? 

We have left the container doors on one of the containers, which is at the opposite end from the entry door. These cannot be opened from the inside. We have also installed windows in the unit, but these have metal shutters across them externally, although they can by removed, but again only from outside.

I am a bit confused as we have a boardroom which is about the same size with only one exit, for example!

Link to comment
Share on other sites

With one door you have an travel in one direction only which means the travel distance should not exceed 18M and the number of occupants must not exceed 60. Also you have created an inner room situation, the factory floor being the access room, so check out https://assets.publishing.service.gov.uk/government/uploads/system/uploads/attachment_data/file/14882/fsra-factories-warehouses.pdf  page 73.

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...