JMFORTUNE Posted March 1, 2019 Report Share Posted March 1, 2019 Risk assessed A small kitchen area with a small 300mm square server hatch to a coffee kiosk. Would this be allowed? As it would contribute to the spread of smoke especially in a kitchen? What are the guidelines on hatches as they are common in kitchens? Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted March 2, 2019 Report Share Posted March 2, 2019 If it is in a FR wall it should be fitted with a FR shutters to maintain the compartmentation. Check out Download RC16B Recommendations for fire safety in Commercial Kitchens . Quote Link to comment Share on other sites More sharing options...
Andy62 Posted March 2, 2019 Report Share Posted March 2, 2019 It is highly unlikely FR will be required for a small kitchen. Quote Link to comment Share on other sites More sharing options...