A Jones Posted February 16, 2019 Report Share Posted February 16, 2019 Morning, hope you can help with a query. A fire risk assessment has highlighted an issue with a teaching lab in our college. The lab accomodates up to 100 students The lab has 2 double exit doors which lead to a lobby area The max travel distance from the lab to the doors leading to the protected stairwell is 35m Area is referred to as normal risk Would you consider the following statement from the FRA to be correct? The main lab on the first floor has the capacity to hold up to 100 occupants. While it has two entrance doors these both lead to the same lobby and therefore cannot be considered alternative exits. Approved Document Part B advises that any room with a capacity of over 60 should have alternative exits. If correct, in order to allow for the occupancy to be more than 60, could we segragate the lobby (with automatic closing double doors highlighted in yellow)? We would also ensure all doors open out. Many thanks Jones Quote Link to comment Share on other sites More sharing options...
A Jones Posted February 21, 2019 Author Report Share Posted February 21, 2019 Any suggestions/comments would be greatly appreciated. Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted February 23, 2019 Report Share Posted February 23, 2019 Providing the double door and screen, meet an 30 minute fire resisting standard and the route through the doors next to it, marked fire exit, lead to a final exit door, then I would suggest you have an alternative MoE. Quote Link to comment Share on other sites More sharing options...
Lyledunn Posted February 24, 2019 Report Share Posted February 24, 2019 I would agree with Mr Sutton. However, the inward swinging doors to the lab would generally mean that occupancy should be restricted ro 60 Quote Link to comment Share on other sites More sharing options...
A Jones Posted February 24, 2019 Author Report Share Posted February 24, 2019 That's what we thought, we'll keep the lobby a sterile area, Many thanks! Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted February 26, 2019 Report Share Posted February 26, 2019 You said "We would also ensure all doors open out and we'll keep the lobby a sterile area" also is the corridor a protected route, if not, then I am not sure if you can achieve the travel distances. This is the the problem trying to give sound advice without the full details and ideally being on site. Quote Link to comment Share on other sites More sharing options...