Corridor doors connected to fire alarms


Allybally888

Recommended Posts

Hi All, I need to connect some doors in a corridor so the residents can't go through them, a code on 1 side and a push button on the other, now this I fully understand, but the home have been told this needs to be connected to the fire panel so when the panel picks up an emergency the doors release from the magnets, I've been advised this can be carried out by connecting a nearby sounder to the door control gear, any help much appreciated 

Alex 

Link to comment
Share on other sites

If it's a care home you don't have them set to all release like that as the risk from resident's absconding, particularly in dementia care, is far higher than in fire. 

As you are using staff to evacuate the compartment of origin they would use the local overrides at each door, leaving the compartments not in fire secure (important as all the staff are busy in the compartment on fire or at the control panel awaiting the fire service). There would be a manual override that would release all the doors at the fire panel as a back up, but properly managed progressive evacuation rarely needs it.

You should seek advice from a third party certified fire risk assessor with decent care home experience who can give advice specific to your situation and importantly put it in your risk assessment.

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...