Landlord testing fire alarm and emergency lighting


Recommended Posts

Posted

Hi - I am trying to establish whether one of our landlords needs to do weekly testing and also the frequency of testing for the alarm panel and emergency lighting. They own a 2 storey Victorian property which has been converted into 3 separate dwellings (bedsits) the tenants only share the communal corridor. Many thanks. Helen

Posted

Fire alarm - weekly testing using different call points in rotaton; 6 monthly service by a competent person with 100% of the system tested over a 12 month period

Emergency lighting - monthly function ('flick') test of all fittings; annual duration (usually 3 hours) test of all fittings. (Don't be conned into a 1 hour part duration test at 6 months, it hasn't been required since 2004 and only wears out the lighting quicker) 

Posted

From my experience regardless of AD B, LACORS, LGA Guide, etc residential of various flavours seems to invariably get a Part1 or Grade A system regardless of the set up!