Guest GUEST Posted December 5, 2017 Report Posted December 5, 2017 A question asked in a FRA template was " where an escape route is a "dead end " are all doors fire resistant and self closing " ? escape route that is a dead end ? surely its not an escape route if its a dead end ?? Quote
Tom Sutton Posted December 6, 2017 Report Posted December 6, 2017 Why not, it is a single direction MoE and all the doors should be FR s/c to enable you to pass the rooms to get to a final exit door. Quote
Guest Guest Posted December 6, 2017 Report Posted December 6, 2017 its possibly me but its surely not a "dead end " if it has an final exit door ?? a dead end is a path that leads nowhere not a path that leads to a door that leads to an open space ? I understand the point of FD leading onto an exit route but its the dead end bit ? Quote
Tom Sutton Posted December 7, 2017 Report Posted December 7, 2017 How does a person get from outside to a room in the dead end, if the dead end leads nowhere. Check out Approved Document B (fire Safety) volume 2: Premises other than Dwelling Houses page 39 diagram 17 show what a dead end is. Quote
AnthonyB Posted December 7, 2017 Report Posted December 7, 2017 A dead end is simply a corridor (or similar) where you can only go in one direction, if you go down the other end you end up against a brick wall. Either it is protected by fire doors and walls to the rooms off it or the whole area is protected by automatic fire detection Quote
Guest Guest Posted December 8, 2017 Report Posted December 8, 2017 Many thanks Tom , makes sense now !!! Quote