Meady Posted December 2, 2017 Report Posted December 2, 2017 If lobby doors leading to a protected stairway are 1200mm, but the stairway is 1000mm, which figure do I use for calculating max. occupancy capacity when using BS9999? Risk profile of building is A2. Also, a strange one, but the clear width of the stairs reduce further to 900mm at the very base! Building is a couple of hundred years old... Quote
Tom Sutton Posted December 6, 2017 Report Posted December 6, 2017 From what you say it is unlikely the buildings was built to BS 9999 so why are you using it for your calculations, it looks like cherry picking. Either way common sense would dictate the narrowest part of an escape route should be used to calculate maximum numbers in that escape route. Quote
AnthonyB Posted December 7, 2017 Report Posted December 7, 2017 As Tom says BS9999 cautions against using it in FRAs in the first place (unless the property was designed and built to it) and against cherry picking which is not accepted. If the premises can meet the whole document in terms of it's design, build and management it's OK to use. You have to go by the narrowest point as if you over occupy based on the higher widths elsewhere you will get a potentially fatal pinch point (as was the case in the layout of the Station Nightclub where many of the 100 dead got stuck in a crush) Quote
Meady Posted December 10, 2017 Author Report Posted December 10, 2017 Thank you Tom and Anthony... Would you recommend I use the DCLG Guides instead? Quote
Tom Sutton Posted December 12, 2017 Report Posted December 12, 2017 I would use the guidance recommended by the Gov.UK DCLG Home Office. https://www.gov.uk/government/collections/fire-safety-law-and-guidance-documents-for-business. Quote
AnthonyB Posted December 12, 2017 Report Posted December 12, 2017 As Tom says. If the Government Guides lead to an untenable situation then Fire Engineering is sometimes an option as is the correct use of BS9999 (in whole not cherry picking sections) - but the later does't always work out. I used BS9999 to try and design out installing a third stair in a conversion of a mill into offices due to excess travel distances, but the upgrading in floor fire resistance, shafts and provision of fire service rising mains associated with a BS9999 design ended up making the traditional benchmark approach easier and cheaper! Quote
Meady Posted December 15, 2017 Author Report Posted December 15, 2017 Thank you guys for your help and guidance - much appreciated. Quote
Guest Robert Posted March 26 Report Posted March 26 Hi I have a building that is used as an open planned art gallery and I have been asked to provide occupancy figure for the space, not normally an issue, however this particular building has three individual entry/exit doors across the front of the building which all lead out onto the same patio type area, and a single fire exit door at the rear of the gallery. To eliminate the largest door from the equation, surely I must have to eliminate all threee front doors, which leaves just the rear exit so the max occupancy is 60. Am I correct or should I just eliminate the largest of the three front doors? Quote