Jump to content

Fire System Maintenance - Leeway


Recommended Posts

Guest Garry Fry
Posted

Good afternoon ,

Is there a one month leeway for fire system maintenance ? we carry out 3 month servicing  and my understanding is that you can carry out the checks one month either side of the due date. Is this correct, I am certain it is contained within BS5839.

Many thanks.

Posted

Nope, you are getting mixed up with BS5306-3 for extinguishers which has a +/- 1 month for basic & extended services.

BS5839-1 states service visit intervals should not exceed 6 months or the system will be deemed to be non compliant. Quarterly servicing hasn't been a minimum requirement for a very long time now.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...