Jump to content

Sliding doors


Richard

Recommended Posts

On a building entrance that has auto sliding doors and which open on fire alarm activation and mains failure with also a staff key override is a green box manual emergency override required.  I see some premises with them and others not. In this particular the main entrance doors opened on approach. The rear staff entrance doors do not as it is only accessed by staff fob key. Neither had a green  box installed on the escape side. Thanks. 

Link to comment
Share on other sites

Sliding doors and magnetic locked doors on escape routes should meet the standards of BS 7273 part 4 which requires a manual override switch (green MCP)  to open the doors if required in an evacuation, with some exception like places of lawful detention but retail premises are not one of them.

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...