clacky Posted June 23, 2017 Report Share Posted June 23, 2017 Can anyone tell me if a set of automatic sliding doors are required to open and stay locked open in the event of a fire activation. These doors are the main entrance to the building but are not classified as a fire exit. Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted June 26, 2017 Report Share Posted June 26, 2017 All doors, required for means of escape, in the event of a fire, which include the main entrance doors, are MoE doors. (Fire Exits) All doors, required or means of escape in the event of a fire, are required to be easily opened, without the need of a key, when the premises are occupied. All automatic doors should be installed according to BS 7036:0 2014/BS EN 16005 2012 which depending on design, require all automatic MoE doors should open and stay open in the event of a mains failure or electrical fault, if a breakout facility is not fitted. For a more definitive answer you need to study the standards more deeply or speak to an expert in this field. Check out http://www.faac.co.uk/productfiles/323_DataSheet_rad0A238.pdf http://www.theadia.co.uk/ Quote Link to comment Share on other sites More sharing options...