Jump to content

Separate Zone For Attic/Loft Area


Recommended Posts

Guest Jay Taylor
Posted

Do you have to have a separate fire alarm zone for the attic/loft area to the floors below?

I know Zones should not cross floors but is the attic/loft classed as a separate floor?

Posted

BS 5839-1:2013
13.2 Recommendations
13.2.1 Recommendations applicable to all detection zones

b) If the total floor area of the building is greater than 300 m2, each zone should be restricted to a single storey.

d) For voids above or below the floor area of a room, these may be included within the same zone of the room, provided that the voids and the room constitute a single fire compartment.

 

Depends whether you class it as a void or a floor. If the space is used and has an access ladder/stair I would be leaning towards calling it a floor, if a disused space more likely a void, but in the case of the latter would want remote indicators fitted.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...