Cable connector housing, fire retardant?


Recommended Posts

Posted

I need to provide a method to connect two wires for a monitored connection from a device to a CIE, but I want that to be a chassis mounted connector on the device so the installer doesn't have to open the box. The connectors themselves are UL94-V0 rated (both the chassis socket and the terminal plug), but the shroud that goes around the terminal plug is only rated to UL94-HB. I'm aware that according to BS5839 pt1 2013 any cable support must be non-combustible if it were a means of cable support, but the primary support for the cable is via the screw terminals in the plug. Is it acceptable to use a UL94-HB shroud in this way?

Thanks,

Mark.

Posted

This type of question can be answer more fully on forum's like http://firealarmengineers.com/.

But I would suggest you consider why the recommendation has been introduced and this should help you to decide if your solution is acceptable. I understand, the reason is, if the cable supports fail in a fire, allowing the cable to fall this could cause a hazard for firefighters. There may be other reasons and you should research why, and see if it will affect your solution.

If fire resistance is the concern then check out the reason why and apply the same logic. 

  • 1 year later...

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...