TD33 Posted August 4, 2016 Report Share Posted August 4, 2016 In my 6 storey building of offices on floors 5 to 6 there are no automatic fire detection systems on these floors but call points. The fire doors on these floors have a 8mm gap with no Instumicent strips or cold seals. However the landing past the fire door do have sensors. Do the doors conform?? Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted August 5, 2016 Report Share Posted August 5, 2016 Fire doors are to prevent a fire and the product of combustion spreading, fire alarms are to alert the occupants there is a fire in the building. The fire doors are not acceptable the gaps are too excessive they should be 3mm +/- 1 mm and fitted with intumescent strips/cold seals. Only call points may be acceptable this will depend on your fire risk assessment. Quote Link to comment Share on other sites More sharing options...