8mm fire door gap.


TD33

Recommended Posts

In my 6 storey building of offices on floors 5 to 6 there are no automatic fire detection systems on these floors but call points. The fire doors on these floors have a 8mm gap with no Instumicent strips or cold seals. However the landing past the fire door do have sensors. Do the doors conform?? 

Link to comment
Share on other sites

Fire doors are to prevent a fire and the product of combustion spreading, fire alarms are to alert the occupants there is a fire in the building. The fire doors are not acceptable the gaps are too excessive they should be 3mm +/- 1 mm and fitted with intumescent strips/cold seals. Only call points may be acceptable this will depend on your fire risk assessment.