TD33 Posted August 4, 2016 Report Posted August 4, 2016 In my 6 storey building of offices on floors 5 to 6 there are no automatic fire detection systems on these floors but call points. The fire doors on these floors have a 8mm gap with no Instumicent strips or cold seals. However the landing past the fire door do have sensors. Do the doors conform?? Quote
Tom Sutton Posted August 5, 2016 Report Posted August 5, 2016 Fire doors are to prevent a fire and the product of combustion spreading, fire alarms are to alert the occupants there is a fire in the building. The fire doors are not acceptable the gaps are too excessive they should be 3mm +/- 1 mm and fitted with intumescent strips/cold seals. Only call points may be acceptable this will depend on your fire risk assessment. Quote
Recommended Posts
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.