Extending A Non Compliant System


Recommended Posts

Guest Jay Taylor
Posted

Hi 

Just wondering if any of you can help...

Is it allowable to add an additional detector to a fire alarm system which is installed in LSF cable (Non compliant with current BS) by using FP200 cable on the new part?

If it is do you note this on the installation certificate that the existing part if non complaint but the new part is complaint?

All advice grateful of.

Thanks

Posted

Thanks for reply AnthonyB

Not sure as yet, we've had a quick look and noticed the detectors are lsf so need to verify the sounders.

I presume if the sounders arent then its a no no?

Is there a part in the regs you can direct me to?

This has all been requested after a risk assessment, but they are no existing certs for the installation.

Posted

If the sounder circuit isn't fire resistant then that's a major non conformity that can affect life safety (plenty of case history of where fire alarm sounders failing early was one of the factors influencing multi fatality fires) and should be a high priority action in the FRA.

Also, unless it's an L1 system if the detection zones are not fire resistant I would want the panel set to operate in the old "short circuit = fire mode" as there would be a risk of a fire in an area not covered by detection destroying the cable putting the panel only into fault and preventing it going into fire.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...