Hi have a shop with flat behind it with its own entrance escape route,and two flats above with their own entrances escape routes.will be upgrading fire barrier to 60 min  .at present have mains aico alarm in each flat with radio link interlinking all flats .there are no common areas.

Posted

If you have a full 60 minute separation between all the flats and shop with no common areas you only require a fire alarm in each flat to BS 5839-6:2013 they do not need to be interlink with other flats. You may or may not require a fire alarm in the shop, dependent on the situation.