Guest Mattf Posted November 17, 2015 Report Share Posted November 17, 2015 Hi, I am hoping somebody on here may be able to help shed some light for me, as I cannot seem to get a definitive answer by myself. I know that according to the offices and shops fire risk assessment guidance, that all doors etc. on the escape route need to be able to resist the passage of smoke and fire to enable escape, my question is this: If an escape route is an enclosed hallway, and this hallway has office rooms leading from the sides of the corridor, does this mean that the doors on the offices need to be fire doors, with intumescent strips installed or something equally as effective, or is it just the fire doors at either end of the corridor that need to be fire doors resistant to the passage of smoke? To me, the escape route starts once you have entered into the hallway, and this is what is throwing me, as I don't know if this means that the doors into/out of the offices into the corridor need to be fire doors, and need to be resistant to the passage of smoke. Any help would be gratefully accepted, Thanks, Matt Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted November 20, 2015 Report Share Posted November 20, 2015 You have a protected escape route and an escape route and it will depend on travel distance/time which you require. If it is a protected escape route all doors opening into that route are required to be fire and smoke resisting if it is an escape route then standard doors are acceptable. In a multi storey building staircases are usually protected escape route which may include a lobby which has to be protected. Depending on travel distance/time, part of corridors may have to be protected but it all depends on the layout of the premises. Quote Link to comment Share on other sites More sharing options...
MattF Posted November 21, 2015 Report Share Posted November 21, 2015 Ok, Thanks Tom. I think from reading into it, i need a protected escape route as the route is a 'dead end' route, with just one way out. Would you say this was accurate? Is there anywhere you can point me so i can find out which type of escape route i need. I need to be able to confidently say which type before i advise my clients as to the reason they require all doors to be fire doors, if that turns out to be the case. Thanks Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted November 25, 2015 Report Share Posted November 25, 2015 If it is a dead end route, you are correct they have to be a protected routes all guidance on MoE will show this. Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted December 14, 2015 Report Share Posted December 14, 2015 If it's an initial dead end an alternative solution to fire doors in the guides is the provision of automatic smoke detection (part of the buildings fire alarm system, not self contained detectors) to every room. Quote Link to comment Share on other sites More sharing options...
Guest Mark Posted October 2, 2019 Report Share Posted October 2, 2019 Hi guys In my place of work they are placing a faraday cage in one of the offices with the entrance being via the office itself which makes it a room within a room which will be occupied frequently. I have questioned where the exit should be as it can be located in a position where occupants can exit straight into a protective corridor leading a fire exit. The project manager has told me she has discussed this with the H+S officer and he is ok with the plans. The plan is to have the door opening into the office and any occupants would then have to exit that door into the office and then exit through the office door into the protected corridor. I think this is incorrect and a breach of the fire regs as the distance they will have to travel from the dead end to an external exit will be increased significantly and therefore slow their exit out of the building. Thoughts anyone>> Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted October 2, 2019 Report Share Posted October 2, 2019 All it sounds like they are doing is creating an inner room, which if travel distances were OK before will remain acceptable. There would need to be one of the following: - Vision panel between inner room & access room; or - Automatic Detection (smoke) to the access room; or - The partition between the inner and access rooms stopping at least 500mm below the ceiling Quote Link to comment Share on other sites More sharing options...