Guest Kevan Posted October 15, 2015 Report Share Posted October 15, 2015 Can you answer this pls we have a bg on every floor, on the ground floor is where I need clarification there is no bg at the bottom of the stairwell but there are no rooms off this landing but a fire door to a lobby there is then a final exit which does have a bg the distance is only 5 to 6 meters from the bottom of the stairs to the fianl exit are we supposed to have a bg at the bottom of the stairs thanks for any advice Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted October 21, 2015 Report Share Posted October 21, 2015 If I understand your description, everybody in the building will have to pass a BG before they leave the premises. Providing they do not have to travel more than 30 metres to reach a BG then the provision of BG's is acceptable. Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted October 21, 2015 Report Share Posted October 21, 2015 Yep, no additional Manual Call Point needed Quote Link to comment Share on other sites More sharing options...