Guest Dora.C Posted October 1, 2015 Report Share Posted October 1, 2015 Hi, We have recently had a fire risk assessment and the recommendation was that we need to upgrade our existing fire doors and electrical intake cupboard doors (they all need cold smoke seals and intumescent strips). Can we use a local experienced joiner to do this remedial work even though he hasn't got a third party fire safety certificate. The report says we need to employ a "Competent contractor" Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted October 4, 2015 Report Share Posted October 4, 2015 In this situation I am not aware of such a thing as a third party fire safety certificate if he/she is a competent contractor and knows what he/she is doing then use them. Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted October 6, 2015 Report Share Posted October 6, 2015 There is such a thing as third party accredited passive fire protection specialists who can carry out fire door improvements, they are usually accredited by schemes such as FIRAS, etc. Checkmate Fire Airfire Controls Gunfire (Gunite) Fire Protection Compliance are all accredited contractors & can certify works. General joiners can be competent and can do the work sometimes, however their is a fair amount of substandard work out there from them. And they should fit the strips to the frame, not the door leaf if at all possible, routing the door leaf is a last resort. Quote Link to comment Share on other sites More sharing options...
Guest Zoe Posted July 14, 2016 Report Share Posted July 14, 2016 When upgrading an existing panelled door (44mm thick) with an Envirograf card and paint system, is it necessary to retro fit intumescent seals? Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted July 15, 2016 Report Share Posted July 15, 2016 From instruction guide AP038-01-2014, REMEMBER THE INTUMESCENT DOOR SEALS, LOCK PROTECTION, AND PROTECTED DOOR CLOSERS! A fire door is not a fire door without intumescent seals on the door or frame, plus intumescent paper must be placed around locks (see Envirograf® Products 69, 71, and 100). Protected door closers should be fitted, such as the all-in-one Envirograf® Product 71A door closer 3-hinge set with factory-fitted intumescent fire protection. Door stops only need to be 12mm thick or less, NOT 25mm THICK! Quote Link to comment Share on other sites More sharing options...
Guest Christopher Clarke Posted July 4, 2017 Report Share Posted July 4, 2017 Dear Sir / Madam, I would like to query how one would upgrade an 30 minute fire door to a 60 minute fire door? Is it a matter of upgrading seals or does the door composition itself need to be different? Any advice would be much appreciated Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted July 4, 2017 Report Share Posted July 4, 2017 Realistically you need a new door! Whilst there will always be the odd exception a 30 minute fire door will be 44mm thick, a 60 minute door 54mm thick. You will find on the internet old guidance on upgrading doors by all sorts of means such as screwing supalux boards onto doors on the fire side, etc, but these are completely untested and cannot guarantee any performance compared to a new third party certified door blank. Not only do you have to consider the door, you have to consider the seals, frame, etc as well Quote Link to comment Share on other sites More sharing options...
Neil Ashdown MAFDI Posted July 4, 2017 Report Share Posted July 4, 2017 When we use the word 'door' in terms of fire doors we mean the complete installed door assembly. An FD60 is very different to an FD30 door in terms of the quality of the components that make up the assembly. In order to upgrade fire separation protection from 30 to 60 minutes it will be necessary to upgrade the entire fire door assembly. Quote Link to comment Share on other sites More sharing options...
Guest Agnese Posted July 7, 2017 Report Share Posted July 7, 2017 Hello, Could you please help me and say must have requirements for fire doors in the office? We are thinking to change our old doors, want to make sure they are in right requirements. Thank you very much Agnese Quote Link to comment Share on other sites More sharing options...
Guest Steve Posted July 10, 2017 Report Share Posted July 10, 2017 Hi just reading this topic and was wondering when/where u use intermittent packers behind hinges, is this essential, what do they achieve? Many thanks Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted July 10, 2017 Report Share Posted July 10, 2017 Without knowing the layout of your offices it in impossible to predict which doors need to be fire doors. You need to speak to the Responsible Person or the person who conducted your fire risk assessment who should be able to inform you, which doors need to be fire doors and the required duration. Quote Link to comment Share on other sites More sharing options...
Neil Ashdown MAFDI Posted July 11, 2017 Report Share Posted July 11, 2017 Intumescent gaskets placed behind the hinge blades will limit heat transfer from the metal hinge to the timber door and frame. They are required for FD60 door installations and sometimes for FD30. Always use the correct type, size and number of screws, its those little fellas that hold the door in its frame! Quote Link to comment Share on other sites More sharing options...