Guest Donna Ash Posted November 19, 2014 Report Share Posted November 19, 2014 Hi, Information seems varied on the topic of fire doors. Basically, looking for clarification that it is OK to not have latches if there is an overhead door closer present on a fire door. Many Thanks Quote Link to comment Share on other sites More sharing options...
Guest Neil Ashdown Posted November 19, 2014 Report Share Posted November 19, 2014 Hi Donna, Yes you are right. Info on fire doors is very varied and this is because the scope of what you can do (and can't do) depends on the fire test evidence for that particular door. So in answer to your question you can have a fire door 'unlatched' and held closed by the self closing device provided that the door has test evidence for that use. Check with the door supplier / manufacturer, if its a new one they should be able to supply certification and product data sheets with the info you need. Any more fire door related questions.........please don't hesitate. Regards, Neil Ashdown Fire Door Inspection Scheme Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted November 19, 2014 Report Share Posted November 19, 2014 Most fire door assemblies fitted with single axis hinges (butt hinges) and fitted with mortise latches rely upon the latch bolt to make an important contribution to the performance of the door in the event of fire, the self-closer alone would not be sufficient. The latch prevents the fire door from distorting in the initial stages of the fire. If you require a fire door without a latch then you would need a pivot hinge and the test details that come with the door should indicate this is possibility. Quote Link to comment Share on other sites More sharing options...
Guest ScottSa Posted May 13, 2015 Report Share Posted May 13, 2015 Hi, re fire doors not needing a latch if a fire-rated self closer is fitted, how can I determine which is a suitable fire-rated closer in this situation? Which fire door closer types are suitable. Are they marked as such, i.e. suitable for use without door latches? Regards, Scott Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted May 14, 2015 Report Share Posted May 14, 2015 The only self closer I have seen that doesn't use a latch is a pivot hinge (floor hinge) which I have seen used on double doors in a corridor. As far as I am aware there is no marking which denotes this and I would imagine you would need to contact the manufacturer to check this out. Quote Link to comment Share on other sites More sharing options...
Guest filip oprisa Posted October 30, 2018 Report Share Posted October 30, 2018 all fire doors at Banatines health spa have NO latches are they breaking the law??? Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted October 31, 2018 Report Share Posted October 31, 2018 Do they have other means of securing the door closed to prevent it opening without requiring a positive action to open it. Quote Link to comment Share on other sites More sharing options...
Neil Ashdown MAFDI Posted November 1, 2018 Report Share Posted November 1, 2018 Unlatched fire doors are common place especially in corridor situations where a latch would be an unnecessary hindrance. Check with the door manufacturers' installation instructions / data sheet that the door has suitable evidence of fire performance 'unlatched'. Similarly, make sure the self-closing device has evidence of fire performance for use with an unlatched fire door. The usual fire rated BS EN 1935 good quality butt hinges are suitable for unlatched fire doors. Section 3 of 'The Code of Practice: Fire & Escape Doors' at http://firecode.org.uk/Code of Practice 2009 Issue 3.pdf provides further information. Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted November 2, 2018 Report Share Posted November 2, 2018 An example of the documentation you should receive when you purchase a certified fire door, http://www.premdor.co.uk/pdf/download-centre/fire-certificates/certifire-cf-195-certificate-of-approval.pdf. If it is not a certified fire door then you could use the services of a fire door inspector. Quote Link to comment Share on other sites More sharing options...
Guest Matty Posted November 27, 2018 Report Share Posted November 27, 2018 Hi. Quick question I hung some fire doors today and my customer is not happy because there is no fire sticky tape around the latch when it’s in the door, is this a legal requirement or not ? Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted November 28, 2018 Report Share Posted November 28, 2018 I do not know what fire sticky tape around the latch when it’s in the door means, what is fire sticky tape? Quote Link to comment Share on other sites More sharing options...
Neil Ashdown MAFDI Posted November 29, 2018 Report Share Posted November 29, 2018 Matty, Are you referring to intumescent gasket material? This material is fitted around the lock-case / latch-case and behind the forend and keep. It is commonly required for use with timber based FD60 doors but not always for FD30 doors depending on the door's test evidence and the lock case size. You should consult the door's data sheet with regard to permitted latch/lock and any requirement for intumescent gaskets. Quote Link to comment Share on other sites More sharing options...