forumsafelincs Posted October 23, 2014 Report Posted October 23, 2014 Hello. I'm fitting fire doors in a house I'm converting to an HMO. The frames are new and have been routed (by the supplier) for combined smoke/heat strips. I'm a plumber by trade but have hung a few doors before but need some advice on these please. I fitted the frame and got everything looking fine and hung the first door with an equal gap of no more than 3mm around the edge. However when I fitted the strips the door wouldn't close easily because of the smoke brush being too proud. To enable it to close smoothly to meet the regs I'd have to plane the door back by 2-3mm. Not only is this going to look very unsightly (a gap of 5-6mm) it then actually exceeds the regulation 3mm gap. Is it possible that the timber supplier didn't rout deep enough for the strip and if so should I just run through it with my router again? The plastic part of the body of the strip stands proud of the frame by about 1mm. If I routed deeper say to make the strip recessed by about 1mm it would solve the problem or is this not recommended. Any advice? Quote
Tom Sutton Posted October 27, 2014 Report Posted October 27, 2014 I was a bricklayer for 10 years and a firefighter specializing in fire safety for 34 years, if you need advice on any of those subjects I will try to help, I only hope there is a joiner on this forum who may be willing to assist you. Quote
Guest LisaVen Posted November 6, 2014 Report Posted November 6, 2014 Hi we have brush smoke seal sin one of our care homes, the residents need hourly checks and are complaining of the noise of the seals when the door is opened and closed. All doors have a 3mm gap around and have recently been renewed, can we cut a shallow groves into the doors to inset the seals to reduce the noise? is there a maximum gap between the door and frame. Quote
Tom Sutton Posted November 6, 2014 Report Posted November 6, 2014 The gap around the door, (two sides and head of door) should be 3 mm, however if the door is a FD30s then that gap needs to be sealed by a cold smoke seal to prevent cold smoke from percolating through that gap in the early stages of a fire. If you sink the cold smoke seal into a grove and it doesn't contact with the frame then its purpose will be lost. Have you tried other types of seal which may prove more silent than the ones fitted now. Quote
Guest Guest Posted July 11, 2015 Report Posted July 11, 2015 Hi there Lisa Did you ever manage to resolve the noisy opening issue. We have a 3 storey new build house and the strips are noisy so considering replacing them with a different make perhaps? Tom what different type of seals would you recommend to try? Quote
Tom Sutton Posted July 13, 2015 Report Posted July 13, 2015 Are you talking about cold smoke seals or intumescent strip seals? Check out http://www.ifsa.org.uk/docs.html Quote
Guest Guest Posted June 23, 2017 Report Posted June 23, 2017 Hi there. Cold smoke seals with the brushes. Quote
Tom Sutton Posted July 18, 2017 Report Posted July 18, 2017 There are two types of seal on fire doors, on door installed after 1987 there is always an intumescent seal, fixed in a groove, which expands when heat is applied to it and fills in the gap between the door leaf and the frame, preventing the fire to pass. Also on some doors a cold smoke seal is fitted, which seals the gap between the door leaf and the frame, which prevent cold smoke from passing through the gap before heat activates the intumescent seal and you can get combination seals both intumescent/cold smoke seals. There is gap between the intumescent seal and the frame which will not cause any noise, but the cold smoke seal which is made of rubber or brushes, has to seal the gap, therefore touches both the door leaf and the frame, which could cause a noise when the door closes. There are a number of different types of cold smoke seals you could try a different one to see if it is less noisier. Quote
Guest Guest Capricorn Estates. Posted July 7, 2018 Report Posted July 7, 2018 Hi been a landlord 25 yrs all HMO properties, it's all down to a good joiner. We fit cold strips is brush / seal strips, almost flush to casing and flush on old doors , where seal is in door. Always mousey and a bit slammy. Fine adjustment twice a year gets it right. Two screws on Briton hinges sorts that. Good joiner or handyman. Cheers. Quote
Guest JO40 Posted August 16, 2022 Report Posted August 16, 2022 I have 2 single 24in fire doors from this 3 storey house. I wish to use them together as a double opening on the middle floor for the Airing Cupboard. I have a bespoke 48in fire frame with fire seals, Sides,Top and all furniture, but :- What do I need to buy for the 3mm gap between the 2 doors? Thanks Joy Quote
Tom Sutton Posted August 17, 2022 Report Posted August 17, 2022 I do not understand your question the 3mm gap is the gap when the doors are installed? Quote