Oli tank barrier


Guest DarrenF

Recommended Posts

I want to position a new oil tank (1100litre capacity) behind a garden raised flower bed wall constructed form old railway sleepers, about 6 inches thick.

The tank will be at least 5 metres away from any building or boundary wall in every other direction.

Would timber this thick provide 30 minutes fire resistance? ( although I have no idea how a fire could get anywhere near the tank!)

Link to comment
Share on other sites

  • 2 months later...
Guest Brandon

Hello,

I am trying to find out if there is a minimum safe working distance for doing hot work (welding/grinding) in the vicinity of a partially full domestic oil storage tank. One of the steel single skin type. Not for working on the tank or pipework, but just in the vicinity of the tank. Is there a fire risk with the vapour in the tank and how far does the vapour travel?

Link to comment
Share on other sites

Domestic fuel oil is similar to white spirit and the flash point of white spirit is 26 to 65 degrees centigrade therefore at normal temperature and pressure it will not give off sufficient vapours capable of igniting. But to be cautious keep the oil tank sealed, place a barrier between your work and the tank like a corrugated steel sheet or a domestic fire blanket.

Link to comment
Share on other sites

  • 3 years later...
Guest BryanMa

Hi - some work has started in a field next to our house. The builders have started bonfires. We have a oil tank on the perimeter of our property. Is there a recommended minimum distance you should have been an oil tank and a bonfire. I suspect they have one fire within 5 metres.

Thanks

Link to comment
Share on other sites

Tank location OFTEC

It is unlikely that a fire could be started by a domestic oil storage tank and its contents. However, tanks are required to comply with fire separation distances in order to adequately protect the stored fuel from a fire or heat source that may originate nearby.

Tanks should be sited:

  • 1.8m away from non-fire rated eaves of a building;
  • 1.8m away from a non-fire rated building or structure (e.g. garden sheds);
  • 1.8m away from openings (such as doors or windows) in a fire rated building or structure (e.g. brick built house/garage);
  • 1.8m away from oil fired appliance flue terminals;
  • 760mm away from a non-fire rated boundary such as a wooden boundary fence;
  • 600mm away from screening (e.g. trellis and foliage) that does not form part of the boundary.

Also this is Bury Council site but you could check your local council see if they can help. http://www.bury.gov.uk/index.aspx?articleid=3559

Link to comment
Share on other sites

  • 3 years later...
Guest MicahelW

Hi,
we had our annual oil central heating audit and service yesterday. The engineer indicated our oil tank does not meet new regulations. I intend moving the tank next year on a base that will meet regulations. However because of its position it will still be near a wooden fence. I need to clad the fence ( I believe will be OK) but I need a recommendation for sheets of material to use. I would like to use sheeting that is above 30 minute standard. 60 minute or above would be great can you help?

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...