Guest KarolB Posted February 4, 2013 Report Share Posted February 4, 2013 Could you please advice on the mounting height of the green break glass override device. Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted February 4, 2013 Report Share Posted February 4, 2013 According to the British standard, Manual call points should be fixed at a height of 1.4 m above finished floor level, at easily accessible, well-illuminated and conspicuous positions free from potential obstruction. They should be sited against a contrasting background to assist in easy recognition. A lower mounting height is acceptable in circumstances where there is a high likelihood that the first person to raise an alarm of fire will be a wheelchair user. Consequentially I would consider a similar rule for green break glass override boxes. Quote Link to comment Share on other sites More sharing options...
green-foam Posted February 4, 2013 Report Share Posted February 4, 2013 Could you please advice on the mounting height of the green break glass override device. Sorry to disagree Tom, but I would say any height you like / find easy. (I say this because as the the OP said, "override device" it's not for a fire alarm, but to over ride an access control system. So is NOT covered by the fire regulations) Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted February 5, 2013 Report Share Posted February 5, 2013 I agree, I didn't say it was covered by the British standard but I think it is reasonable to use the same guidance. Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted February 5, 2013 Report Share Posted February 5, 2013 In light of green-foam's submission I did further research and found green break glass override boxes are subject to BS 7272 part 4 2007 and 12.2.4 states that the height should be 1.2 m from the floor level and be within 2 m of the associated door. There are other conditions but you need to check the British standard for the full details. Sorry for my previous submissions. Quote Link to comment Share on other sites More sharing options...
Guest david pooley Posted August 28, 2013 Report Share Posted August 28, 2013 we think we may have to move a break glass unit from a new meeting room that we are forming inside a larger office for which it functioned. there is also another bgu located in a lobby within 3 to 4 metres of this bgu. would we have to move the bgu from its current location to a corresponding new location in the new offce i.e. the remianing office area outside of the new meeting room ? many thanks. david pooley Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted September 1, 2013 Report Share Posted September 1, 2013 Without seeing the location of all the Manual call points I cannot comment on your particular situation but siting of Manual Call Points should be as follows. Break Glass Call Points should be mounted 1.4 m from the floor, sited where they can be easily seen and on exit route from the building. BGU's should be sited on the floor landings of stairways and at exits to open air. It should be noted that many Fire Officers prefer BGU's to be fitted on the floor side of an access door to a staircase so the floor of origin is indicated at the Control Panel. Where necessary, extra points should be sited so that the greatest travel distance from any point in the building to the nearest call point does not exceed 30 m. A greater number of Call Points may be needed in high risk areas or if the occupants are likely to be slow in movement. Quote Link to comment Share on other sites More sharing options...
Guest GeorgeBla Posted March 20, 2014 Report Share Posted March 20, 2014 Could you clarify if break glass security on fire exit door is acceptable to local authorities thanks Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted March 21, 2014 Report Share Posted March 21, 2014 George you need to speak to the local authority, they are the only ones able to give that answer and what do you mean by "break glass security on fire exit door"? http://www.firesafe.org.uk/security-and-fire-safety/ Quote Link to comment Share on other sites More sharing options...
Guest Ben Evans Posted January 30, 2016 Report Share Posted January 30, 2016 Should there be a BGU at each exit of a building ? Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted February 2, 2016 Report Share Posted February 2, 2016 The BS says you should not be able to leave the building without passing a BGU which usually means a BGU adjacent or close to all final exits. Quote Link to comment Share on other sites More sharing options...
Guest George Posted October 2, 2018 Report Share Posted October 2, 2018 The British Standard is BS7273 part 4 Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted October 17, 2018 Report Share Posted October 17, 2018 The BS I quoted from is BS 5839-1:2013 but the current one should be similar and yes they should be a BGU at each exit of a building. Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted October 17, 2018 Report Share Posted October 17, 2018 One change in the 2017 edition is that exits that do not lead to an ultimate place of safety don't need a call point, e.g. a door onto an internal courtyard with no further escape. Quote Link to comment Share on other sites More sharing options...
Guest Richard Posted January 5, 2020 Report Share Posted January 5, 2020 Hi If an already existing call point has been fitted to close to a wooden dado rail and is unable to be tested could I just it 180 degrees so that the test key can be inserted from the top? Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted January 7, 2020 Report Share Posted January 7, 2020 As you would be fitting the call point upside down I would contact the manufacturer to check that it would work correctly in that position and as a result any wording on the face of the call point would also be upside down, therefore you then need to ask your self could this cause confusion for any person who had to use the call point. Have you considered modifying the dado rail to enable the test key to be used satisfactorily or relocating the call point a few cm higher. Quote Link to comment Share on other sites More sharing options...
Guest Alison Posted September 4, 2020 Report Share Posted September 4, 2020 Hello All, I am currently conducting a project and am trying to find information on the height of fire emergency door release button/break glass button. I was wondering if there was any guidance around the height of the button in Special Schools or Mental Hospitals. I work in a special school and the fire alarm is pressed quite often and I was wondering if we could make them higher or if it would be worth looking at other ways to cover them. We currently have then cover with a plastic lift up cover. Thank you for any help in advance, the internet isn't being helpful. Alison Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted September 5, 2020 Report Share Posted September 5, 2020 In certain circumstances key operated call points are permitted, your appointed fire risk assessor should be able to come up with a set of options. Does the premises have extensive smoke detection? Quote Link to comment Share on other sites More sharing options...
Guest Alison Posted September 16, 2020 Report Share Posted September 16, 2020 We do have extensive smoke detection on the premises. Quote Link to comment Share on other sites More sharing options...
AnthonyB Posted September 17, 2020 Report Share Posted September 17, 2020 Then there are options open to you, your fire risk assessment would need to justify this but it's not impossible. Quote Link to comment Share on other sites More sharing options...