Kevin Shields Posted August 22, 2011 Report Posted August 22, 2011 Is it compulsory to have Emergency Lighting in Low Rise Communal Areas? We have Emergency Lighting in all our High Rise Multi Storey Blocks however the guidance we have on Low Rise doesn’t state if we need it more that it’s desirable. Quote
Tom Sutton Posted August 22, 2011 Report Posted August 22, 2011 It all depends on the risk assessment some buildings may require emergency lighting others not. When a fire risk assessment is conducted in the common areas of blocks of flats the need for emergency lighting will be identified in the documentation, assuming you are not conducting the FRA yourself. Check out the DCLG Sleeping Accommodation guide, Section 5 for more information. A link to the guide can be found in http://www.firesafe.org.uk/regulatory-reform-fire-safety-order-2005/ plus other relevant information. Quote
Kevin Shields Posted August 23, 2011 Author Report Posted August 23, 2011 Thanks Tom. Our risk assesment recomends them but doesnt stipulate if they are legally required. Thanks again Kevin Quote
Tom Sutton Posted August 30, 2011 Report Posted August 30, 2011 Certainly a legal requirement check out article 14 (h) of The Regulatory Reform (Fire Safety) Order 2005 Quote