jagjeevan sansoa Posted February 7 Report Posted February 7 Hi Mr Sutton seeking you advice We have plant room doors to block of flats recently damaged due to an incident-- theses quite old and need replacing do we need accredited installer ? do vents need to fitted to doors as legal requirement kind regard Jag Sansoa Quote
green-foam Posted Saturday at 14:27 Report Posted Saturday at 14:27 Jag, on any forum it is never a good idea to direct your question to a specific forum member, the reason is, as demonstrated in this case, Tom Sutton last posted in November 2022 so will never read or reply to you. The admin on this site is not as good as it could be, hence your question was allowed with no notification to you. Quote
AnthonyB Posted Saturday at 21:27 Report Posted Saturday at 21:27 You should ideally use an accredited installer to ensure that a certified doorset is correctly specified and installed (although admittedly it's no guarantee). Vents should be avoided unless the room includes plant requiring a minimum specification of ventilation (e.g. boilers) & there is no alternative such as external wall vents. If a fire door (e.g. FD30) they should be intumescent vents or if a firedoor also requiring smoke control (e.g. FD30s) then you would need the vent to be protected by an automatic fire and smoke damper linked to the fire alarm system, usually with detection either side. Quote