Andy Mack Posted September 18, 2024 Report Posted September 18, 2024 I understand it a latch bolt must overcome the strike plate, stay in position (positive latching) and opened manually from the inside with a lever/handle and outside with a key or code etc. My concern is that the roller bolt does not automatically lock into position and can move freely. Theres no unlatched test evidence for the door but if the self closing device is able to keep the door closed against the frame is it acceptable? Quote
Neil Ashdown MAFDI Posted September 20, 2024 Report Posted September 20, 2024 Roller bolt type latches are not usually fitted to fire doors. Section 6 of the document 'Code of Practice: Hardware for Fire & Escape Doors' deals with latches and the many fire door related issues concerned with the different types. The document is available online at http://firecode.org.uk/Code_of_Practice_hardware_for_fire_and_escape_doors.pdf Below is particular commentary on Roller Bolt Latches Quote
Andy Mack Posted September 20, 2024 Author Report Posted September 20, 2024 7 hours ago, Neil Ashdown MAFDI said: Roller bolt type latches are not usually fitted to fire doors. Section 6 of the document 'Code of Practice: Hardware for Fire & Escape Doors' deals with latches and the many fire door related issues concerned with the different types. The document is available online at http://firecode.org.uk/Code_of_Practice_hardware_for_fire_and_escape_doors.pdf Below is particular commentary on Roller Bolt Latches Fantastic just what i needed. ive identified the item as a yale 81 rollerbolt nightlatch Quote