Guest Perry Pattison Posted July 14 Report Posted July 14 Fire door installed 2011 comes with full paperwork stating FD 30/60 and has upvc frame fully steel reinforced and intumescent strips. Does this still comply with latest regulations.?. Quote
AnthonyB Posted July 15 Report Posted July 15 AS long as the paperwork says a uPVC frame is actually acceptable and it was installed in accordance with the manufacturer's instructions using their approved compatible components and is still in undamaged working order then yes. Depending on location it may have been meant to have been installed with smoke seals and also it's either a 30 minute door or a 60 minute door it can't be both. Quote
Recommended Posts
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.