54321M Posted October 26, 2023 Report Posted October 26, 2023 After any advice from the forum 🤞 We have many external front entrance FD30 doors to replace that have have services passing through the existing glazed fan lights. The client will not relocate any services and our door supplier only has testing under UKCA for a full width fan light section. There is no fire consultant or building control involved so at a loss at the moment. I am struggling to find a solution that would allow us to create a tested partition detail and certify the door set alongside. I have spoken with Promat but they need steel section installing to separate from the door set which is a huge task and additonal cost to the project. Could anyone point me in the right direction or has experience of this from previous projects? Thanks in advance Quote
Neil Ashdown MAFDI Posted October 30, 2023 Report Posted October 30, 2023 The door supplier is correct that its very unlikely that any fire door set will have evidence of fire resistance performance with fire-stopped services passing through any part of it. On the flip side there are many fire-stopping products with certification for fire resistance performance when used with cables and pipes passing through walls. Consult a fire-stopping specialist for advice. Quote
Recommended Posts
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.