Deta 1163


Recommended Posts

Posted

I have two Deta 1163 smoke alarms. One is upstairs and the other one downstairs. I have changed the batteries and tested both of them and they are working. The one downstairs shows a constant green light only and the one upstairs displays a constant green light plus a flashing red light with no noise. Is it correct for them to be different as I think they are conected or is one of them not working.

Posted

The green light indicates there is mains present.

The red LED should flash once every 30-40 seconds to indicate all is well.

The red LED will flash once every 8-10 seconds if the alarm has been silenced

The red LED will flash once a second (and the sounder will be operating) if the unit is in alarm condition.

What happens if you press the test button?

 