Guest Posted April 21, 2009 Report Share Posted April 21, 2009 As a business user - normal office - why do I need an annual inspection/maintanance visit when the unit has a 5 year warrenty? Thanks A.M Quote Link to comment Share on other sites More sharing options...
Garry Webster Posted April 21, 2009 Report Share Posted April 21, 2009 Dear A.M The British Standard BS5306-3 requires yearly inspection. If you are a business, your own fire risk assessment will usually refer to this standard and your business insurance will usually require this standard. The five year warranty just means that if the unit is faulty within the 5 years, we will replace the unit or repair it for free. Kind regards Garry Quote Link to comment Share on other sites More sharing options...
Guest alif Posted March 12, 2015 Report Share Posted March 12, 2015 Is it a regulatory requirement to change extinguisher tags & rings each year on inspection? Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted March 12, 2015 Report Share Posted March 12, 2015 BS 5036 pt 3 2009 says you should reassemble according the manufacturer instruction also replace with new any safety clip and indicating device designed to show if the extinguisher has been operated. Quote Link to comment Share on other sites More sharing options...
green-foam Posted March 13, 2015 Report Share Posted March 13, 2015 Thinking out loud. Tom, what if the extinguishers in question are stored pressure. The engineer could not take anything apart, there for has no need to change the anti tampering tag. Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted March 14, 2015 Report Share Posted March 14, 2015 Green-foam, I agree, but I am just quoting the BS, but common sense says why! If you haven't damaged the tamper tag why replace it? I think the problem is, they are trying to deal with different types of extinguisher with the same clauses and I believe you need to apply common sense at times. Quote Link to comment Share on other sites More sharing options...
Shawn Bosworth Posted March 18, 2015 Report Share Posted March 18, 2015 As part of the basic service you have to remove the safety device (pin) to ensure that it moves freely and check that the handle also has free movement. To do this you must break the tamper seal. This applies to all extignuishers, stored pressure and cartridge operated. Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted March 18, 2015 Report Share Posted March 18, 2015 I stand corrected Shawn as you say, remove the safety device (pin) to ensure that it moves freely and check that the handle also has free movement is in accordance with the BS but why would you need to replace the pin, can it become damaged when you try to remove it? Quote Link to comment Share on other sites More sharing options...
Guest chogs Posted March 18, 2015 Report Share Posted March 18, 2015 You would need to replace the pin on chubb type units that have a breakable indicator attached. Quote Link to comment Share on other sites More sharing options...
Guest SuzanneJ Posted March 30, 2015 Report Share Posted March 30, 2015 hi, I wonder if you can advise who is correct, I am querying my head offices view on the testing of fire extinguishers, I think the MUST be done every twelve months, but my HO say that they can be serviced upto 6months after the 12 months is up, meaning it can be upto 18 months before its serviced, - stating this is in line with legislation Can you confirm what is correct? Thank you for your help Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted March 30, 2015 Report Share Posted March 30, 2015 As far as I am aware and according to BS 5306 part 3 2009 you are required to service all extinguisher (basic service) every twelve months (+/- one month) from the date of commissioning or last service. The extended service is slightly different, for all extinguishers except CO2, it is five years from the date of commissioning or 6 years from the date of manufacture which ever the sooner and then every five years. For the full information you should read BS 5306 part 3 2009 and if they have used other guidance you should ask what guidance. Quote Link to comment Share on other sites More sharing options...