Posted

In a commercial premises, can combustible items be stored under fire exit stairs, providing an alternative escape route is available? Or should flammable objects never be stored under escape stairs?

 

Thanks!

Posted

Combustible storage in escape stairs is to be avoided. Even for accommodation stairs it is best to keep it to the absolute minimum, and limit ignition sources.

If the stairwell is the only area for receiving goods in, then it has to be managed carefully, and firmly!

Storage of sack barrows and other predominantly non-combustible equipment can be tolerated if there is sufficient space to keep it well out of the pedestrian route. 

Posted
On 24/07/2023 at 17:33, AdamR said:

In a commercial premises, can combustible items be stored under fire exit stairs, providing an alternative escape route is available? Or should flammable objects never be stored under escape stairs?

 

Thanks!

If the stair is a protected route then it should be free from obstruction & clear of combustibles (your fire risk assessment and if the building is modern enough the fire strategy will determine this).

Non combustible items could be tolerated but require careful management and monitoring as when people see some stuff stored there they tend to assume they can add to it and combustibles can start to creep in!

 


In the old days of the Fire Certificate combustibles in a protected stair would be a breach of the certificate and thus an offence. 

  • 11 months later...
Guest FMC999
Posted
On 01/08/2023 at 20:57, AnthonyB said:

If the stair is a protected route then it should be free from obstruction & clear of combustibles (your fire risk assessment and if the building is modern enough the fire strategy will determine this).

Non combustible items could be tolerated but require careful management and monitoring as when people see some stuff stored there they tend to assume they can add to it and combustibles can start to creep in!

 


In the old days of the Fire Certificate combustibles in a protected stair would be a breach of the certificate and thus an offence. 

if the escape route is being used as an "office" what contravention is in place, trying to provide reason ( Law) why as the cant do what they are doing. Photocopiers, desk, telephone etc place in escape route.

Thanks

escape route.msg

Posted

It depends on the size and layout of the premises as to whether that needs to be a protected route, however it should be avoided in any case.

The bit of the legislation covering this is in Article 14 of the Fire Safety Order:

Emergency routes and exits

14.—(1) Where necessary in order to safeguard the safety of relevant persons, the responsible person must ensure that routes to emergency exits from premises and the exits themselves are kept clear at all times.

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...