Paul B Posted June 20, 2023 Report Posted June 20, 2023 Hi All Is it necessary to have AFD in a lift shaft where the motor and associated components are enclosed in the lift shaft and not in a separate location? Should there also be AFD on each floor within a certain distance of the lift entrance? This is a three storey multi occupied office building with the lift located in a protected storey exit. Many thanks for your advice. Quote
AnthonyB Posted June 21, 2023 Report Posted June 21, 2023 What category is the system intended to meet? Quote
AnthonyB Posted June 26, 2023 Report Posted June 26, 2023 In which case yes to both as per paragraph 22.2(c) of BS5839-1:2017 Quote
Recommended Posts
Join the conversation
You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.