Jump to content

How often do we need to certify emergency lighting?


Guest JohnRo

Recommended Posts

In our block of flats, a competent person does the monthly functional checks and one hour test 6 monthly. Annual checks are done by a company who can issue a Certificate.

We are now told that the latter is legally required six monthly

Is this correct ?

John

Link to comment
Share on other sites

  • 8 months later...
Guest Jamiew

Dear Sir can you advise what you would recommend/legislate for regular emergency light testing. are we obliged to carry out monthly flick tests, a 1 hour test and also a 3 hour test every year? Should we meet regualtions with one of these tests or all of them? Many thanks

Link to comment
Share on other sites

According to the appropriate British standard BS EN 50172:2004 / BS 5266-8:2004 Emergency escape lighting systems. Specifies the minimum provision and testing of emergency lighting for different premises,it should follow the following procedure.

Daily emergency lighting inspection (only for central back-up systems)

This check only applies to emergency lighting systems with one central back-up battery system. In this case, there is a daily visual inspection of indicators on the central power supply to identify that the system is operational. No test of operation is required. This test does not apply to emergency lighting with self-contained back-up batteries in each unit (standard emergency lighting).

Monthly emergency lighting tests

All emergency lighting systems must be tested monthly. The test is a short functional test in accordance with BS EN 50172:2004 / BS 5266-8:2004.

The period of simulated failure should be sufficient for the purpose of this test while minimising damage to the system components, e.g. lamps. During this period, all luminaires and signs shall be checked to ensure that they are present, clean and functioning correctly.

Annually

A test for the full rated duration of the emergency lights (e.g. 3 hours) must be carried out. The emergency lights must still be working at the end of this test.

The result must be recorded and, if failures are detected, these must be remedied as soon as possible.

Check out http://www.firesafe.org.uk/emergency-lighting/

Link to comment
Share on other sites

  • 9 months later...
Guest Guest

I have recently joined a fire company and I have been told that Fire alarm systems and Emergency lights have to be tested twice a year by a qualified engineer. I have read your previous notes but I am now confused, as the people around me have a wealth of experience.

Link to comment
Share on other sites

  • 9 months later...

A person is to be regarded as competent, where he has sufficient training and experience or knowledge and other qualities to enable him properly to carry out any such duties assigned to him.

That the easy bit, how you select a competent person that’s the hard bit. First what professional qualifications he/she have is a good starting point, do they have independent recommendations which you are able to check out. Is insurance available if things go pear shaped and you must also consider at least three candidates to assess the average cost of the service which will ensure you are not being overcharged. It is the same as employing any other contractor you must do your research.

Check out http://www.bafe.org.uk/schemes.php it is not a guarantee but it is one of the few qualifications available for many fire safety professions.

Link to comment
Share on other sites

  • 1 year later...
Guest Supa sparks

If in doubt always use a person or firm that are registered under the Competent persons scheme.

NICEIC, or  Nappit are a good start, both verify the qualification of members and also do an annual inspection.

Link to comment
Share on other sites

  • 1 month later...
  • 8 months later...
Guest Philippa

Just to be clear, if the monthly and annual checks (which we can ourselves) do not raise any issues, does the system need any routine servicing from an electrician?

Thanks!

Link to comment
Share on other sites

  • 1 year later...
Guest David Mclean

Just discovered your site . Excellent. We are in a court of 6 separate blocks, with 4 flats in each block.

We are 27 years old and just had our entrance lights to each block replaced .They called it 'emergency lighting .'

Much better .Lights come on automatically, and we are wellpleased .

They now tell us we have to have them checked etc at £240  a year .Is that right ?  We never had to do that with the old lights .

It is to do with emergency light rules regulations. But do we come under that regulation? Surely we are too small. 

Any advice appreciated .

Thasnking you

David Mclean

Link to comment
Share on other sites

Size of premises has no bearing on applicability of legislation. Even a tent in a field if not used as a private dwelling is subject to fire safety legislation.

If your fittings are genuine emergency lights (that will stay illuminated upon power failure using their internal batteries and can often be identified by their green LED light (which is illuminated under normal conditions to show the battery charger is on) then they require a suitable system of maintenance under the Fire Safety Order. The benchmark is in BS5266-1 where the fittings should be tested monthly for function (brief on/off test) and annual for duration (full 3 hours under battery).

If the installation has been made by a competent person and in line with BS5266-1 then there will be secret key test switches that would allow you to carry out this testing.

Link to comment
Share on other sites

  • 1 month later...
Guest EML Testing
On 28/09/2012 at 15:44, Tom Sutton said:

You are not required to do a 6 monthly test, daily monthly and annually who ever told you ask them to check the latest British Standard, BS EN 50172:2004 BS 5266-8:2004.

 

Check out http://www.firesafe....gency-lighting/

Check out each of the HM Gov Guides to Fire Risk Assessment - Appendix A

Link to comment
Share on other sites

BS 5266 part 8 2004 is clear there is no six monthly test only the daily, monthly, annual test and the regulating authority may require specific tests. I think the gov guide is incorrect and I am not surprised.

I do accept my wording could be better but if you read the following submission in June it is clear and if the link was checked out it is quite clear there too.

 

Link to comment
Share on other sites

  • 8 months later...
Guest Pellis5582

For annual testing, is there 30 days grace as it's not always possible to get to a site on the same date ever year, or does it have to be done before the previous cert runs out?

Link to comment
Share on other sites

  • 3 months later...
  • 1 year later...

Hello,

 

I am the resident of a small residential development and I also look after the communal areas on behalf of the owners - i.e. I look after the management company.

 

Last year, an electrician installed new LED emergency lamps across the our development (which is comprised of three small blocks). These replaced a series of old fluorescent emergency lamps. He also installed a test switch in each area.

I’ve been running and recording the required monthly checks as required and we have just reached our 12 month anniversary of the new lamps, so the annual test is now due. I have read this thread several times, and I still cannot seem to understand whether we definitely need a professional organisation to carry out the three hour test or whether I can do it myself? Of course, if there are any faults found over the course of the annual test then I would bring-in the electrician to make the necessary adjustments and repairs.

Please can you advise me whether I am able to carry out the annual test myself without professional intervention?

 

Additionally, we have a smoke ventilation system (AOV) in the each of the three small blocks. I check that the vent opens and closes via the manual switch every month, at the same time I test the emergency lights, but I presume I need to test the smoke sensor on an annual basis using a smoke generating machine. I cannot find any information about the formal necessary testing of this system, so would be grateful if somebody can guide me towards the necessary legislation.

 

Thank you, in advance, for any help you can offer with these matters.

Gary

Link to comment
Share on other sites

  • 2 months later...
Guest Melix

Hi there.  Do large warehouses need emergency lighting or would glo-in-the dark floor strips or specialist paint be sufficient to aid a persons escape?

Link to comment
Share on other sites

Join the conversation

You are posting as a guest. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...